Dr. Venkman said:
Quote:
He basically put it what he had available. Could have damaged the breaker and swapped with something in the truck. Supply chain issues, etc.
He did the NEC calculation and it told him 125A so he put that in. If so, then I'm sure he also pulled 125A cable.
HUZZAH!
If the original electrician put in larger wire out of the kindness of his heart I'll eat your hat. Just because "a lot" of new homes have 200A panels doesn't mean they all need them, especially with gas appliances. Quite a few utility companies own and maintain the service lateral, which is the set of conductors from the transformer or handhole to the meter. They follow their own standards based on real world diversity factors, which will be smaller than the service equipment main panel and everything downstream in your house. It's entirely likely a new home with a 200A panel is fed by the utility with wire only good for a hundred and change.
I'm in a Powerpoint from hell meeting and bored.
Lighting/receptacles 2700 x 3VA/sqft = 8100 VA
Small appliance 2 x 1500 = 3000 VA
Laundry 1 x 1500 = 1500 VA
Dryer 7200 VA
Microwave (assuming built in above stove) 1800 VA
Dishwasher 1800 VA
Disposal 1800 VA
Fart fans 3 x 50 = 150 VA
Total 25,350
NEC 220.82 Optional Calc for Dwelling Unit
25,350 10,000 = 15,350
15,350 x 40% = 6,140
General load total 6,140 + 10,000 = 16, 140 VA
Service total:
General 16,140
Gas furnace, hp motor 1000 VA
4ish ton condensing unit 8400 VA
Service total = 25,540 VA
25,540 VA / 240V = 106A
Next size standard breaker is 125A.
OP,
Tell that electrician you are going to pursue the "undersized" panel with the builder. Ask him to provide an NEC calc to justify a 200A panel. If he stutters, hand him the above and then Conner McGregor walk around him and tell him to GTFO*.
* provided you don't have a bunch of other equipment or a pool.