tgivaughn said:
Bath GFICs are NOT supposed to support hair dryers that today run in watts similar to 1/2hp motors!
IF also the MBR outlet trips then my prime suspect is the electrician and poor mgt builder that included that nearby outlet unproperly in that prudent bath circuit to save themselevs time/money.
Spec/tract house?
If "custom" please cite names so all can avoid such profiteering.
Hoping its just a bad profiteering part and cite ,,, TEMU/China = SOP?
Holy stream of consciousness Batman.
Now why exactly would a, say 15A GFCI, not be able to handle a 15A load? The plug on the end of that Harinator 5000 blower means something. Unless it has the two prongs going in two different directions (one up and down, then one sideways) then it's a 5-15P and you can run it all day long on a 15A receptacle, GFCI or otherwise.
OP isn't resetting the breaker, so it's not an overload issue. GFCI's will trip for two reasons: it's seeing more than a nominal 5 milliamps of differential current between the phase and the neutral, or the GFCI has failed and it thinks it's seeing more than 5 milliamps. The problem is there are a lot of ways to get to 5 milliamps.
As Ben noted you get capacitive leakage in long circuits downstream from the GFCI. It's called preloading. And then you have two of the biggest offenders for leakage currents in appliances - heaters and motors - put together in the blow dryer.
OP said the two appliances popped the GFCI. A little leakage from the blow dryer, a little from the straightener, a little on the circuit equals pop.
Then then blow dryer by itself popped in MBR.
The blow dryer by itself in guest bath, where the GFCI is, worked just fine. That tells me it's probably not the blow dryer by itself, but a combination of blow dryer and preloading on the circuit going from guest to MBR. Replacing the GFCi won't hurt, but you might still have a challenge.
Try plugging both blow dryer and straightener into guest GFCI receptacle. If it pops, you have leakage in the appliances. Not a huge deal, it happens with heating elements. I've had a kitchen equipment manufacturer flat out tell me their widget cannot go on a GFCI protected device. Next try plugging the blow dryer and straightener into a different GFCI. If it pops again, then it's not a device issue.
As far as Temu or whatever that was, it's not how I would wire it, but most homes, production and custom, will have one GFCI device protect receptacles in multiple bathrooms, or a bathroom and a powder room. It comes out of a code requirement on how you have to isolate bathroom receptacle circuits.